    I have this French Legrand interrupteur.
    Turn it over and there are three of these push fit buttons on the back.
    Red (L) in, right next it is a white button (1) out, and at the other end a single white button (2) out.
    Just to be safe, for two way switching only, is the out wire to the one light connected to (1) or (2) or doesn’t it matter for two way switching?
    Thanks


    #1796080
    tomdenne
    tomdenne
    Participant
    Joined: 29 Oct 2008
    Location: 58 La Nièvre
    Total posts: 4459

    It doesn’t matter.


    Tom

    #1796095
    loopski
    loopski
    Blocked
    Joined: 23 Jan 2013
    Location: deux sèvres
    Total posts: 9778

    True!
    But it would if he was connecting a security light with a PIR.


    I would lie on top of the stairs and smell the cigar smoke of Castro.

    #1796103
    badger
    badger
    Participant
    Joined: 04 Dec 2008
    Location: Near Vire (14)
    Total posts: 1408

    Just to be safe, for two way switching only, is the out wire to the one light connected to (1) or (2) or doesn’t it matter for two way switching?

    Umm…..if you really are talking two way switching (va et vient) then neither 1 or 2 goes to the light. The following happens at one switch:

    • L = the live supply of the lighting circuit.
    • 1 = one of the two “navettes” bewtween the two switches.
    • 2= the other of the two navettes.

    At the other switch you have:

    • L = the switched live to the light.
    • 1 = one of the two “navettes” bewtween the two switches.
    • 2= the other of the two navettes.

    However, if you really meant to ask about single switching then your original assumption is correct, but do always try to make the off position the one with the top of the switch pressed in/up.


    Jonathan Badger - St Germain de Tallevende 14500 http://www.badgerlx.fr

    #1796140
    Avatar
    willythecat
    Participant
    Joined: 23 Jul 2013
    Location: france
    Total posts: 63

    Thanks everyone, replies most helpful.

    Regards


    • This reply was modified 02 Oct 2017 08:44 by  willythecat.
French Electrical & Other Building Issues
Viewing 5 posts - 1 through 5 (of 5 total)

You cannot reply to this topic.